(0)| 9/25/2022 3:11 AM | |
|
Joined: 12/18/2014 Last visit: 1/15/2026 Posts: 36457 Rating:
|
Attached is an example. The 4-20 mA signal is scaled with the analog amplifier B001. The load is released or shed with the analog threshold switch. If output Q1 has a high signal, the load is released. If the current is greater than 15.00 A, the load is shed (Q1 = off). If the current then falls below 12.00 A, the load is released again (Q1 = on). The threshold values for release or shedding can be changed via the display (or TDE). AttachmentLoad Shedding_0BA8.Standard.zip (665 Downloads) |
| 9/30/2022 2:10 AM | |
|
Posts: 3 Rating:
|
I don't really have the space to add more controllers. The 4 heaters are already each on their own output for staging, can they not also work for load shedding? |