Hi I have similar question I have motor module 6SL3120-1TE13-0AD0 that I need to replace (it measure 100VDC but it should show 580V). I don't have exact same module. I have modules with same electrical parameters: 6SL3120-1TE13-0AA4 (I tried with this) 6SL3120-1TE13-5AA3 and I have project in TIA15.1 I tried in offline replace module in hardware configuration. I changed in section motor module selection, and it compiled without errors - is enaugh that i need to do? If there are no errors that means it should work? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/11/2022 10:03:04New subject after splitting |
|
10/12/2022 11:42 AM | |
Joined: 10/11/2006 Last visit: 9/8/2025 Posts: 6039 Rating:
|
Hello bartekle, Because this is no 100% identical drive I would personally check the drive parameters again, to make sure everything is still on the desired setting and to adapt parameters which could be affected by the lower overload capability. Please be aware that the motor plug is different of both replacing modules compared to 6SL3120-1TE13-0AD0. |