Hello rabindra_rabi, Since your PT ratio is 33KV/110 volt, relay resets when pick up voltage reaches to set volt i.e. 110V. So the relay function & parameter setting are correct. I would suggest you to check why HT 33KV voltage increases (normally it should not be more than 34.5 KV) up to 36.3 KV (equals to 125 Volt) ? |
| 1/13/2023 1:49 AM | |
|
Posts: 7 Rating:
|
Drop out value is settable thrugh dropout ratio parameter. Reference it takes is setting stage value,not the PT ratio defined in the relay. |
| 1/13/2023 1:59 AM | |
|
Posts: 7 Rating:
|
Device driver/parameter set version for a specific relay can be downloaded from Siemens online support. |