1/18/2023 10:48 AM | |
Joined: 12/23/2015 Last visit: 4/22/2025 Posts: 4 Rating:
|
I am trying to read up to 15 gas monitors, via Modbus using MB_CLIENT. I have no problem communicating with the first one, but when adding further monitors, these go into error 16#80C8. The help information shows the error as below:
I cannot work out how to rectify this error, as all settings for the further gas monitor MB_CLIENT blocks are the same. Any help would be greatly appreciated. Attachmentmodbus testv1.zip (566 Downloads) |
1/18/2023 12:08 PM | |
Joined: 8/12/2021 Last visit: 8/20/2025 Posts: 351 Rating:
|
Hi jezzwad! It is strange that you can only communicate with the first station, have you checked that the configured identifiers of the Modbus client block are correct, what is the value of the STATUS parameter? I suggest you check the configuration of the block based on the manual and add an error logic, saving the status value in an auxiliary flag to be able to analyse it.
|
If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
1 thankful Users |