(0)| 10/1/2018 6:55 AM | |
|
Joined: 10/16/2007 Last visit: 12/11/2025 Posts: 658 Rating:
|
Hello, sometimes it helps if you switch of and on again the system. Regards Scott |
| 10/1/2018 8:16 AM | |
|
Posts: 5521 Rating:
|
hi ganz11, have a look in the manual of the ET200M-module: SIMATIC Distributed I/O device ET 200M On Page 185 you will find the diagnostics with the LED-display. When the BF-LED flashes, it means: IM 153-1 is incorrectly configured - no data or The configured structure of the ET 200M check the projected HW-config of the station and the DIP-Swiches for the PB-address. The IM153-2 needs a Powercycle after you changed the PB-address. Also check the Profibus at all. hope this helps, regards, |