(0)| 2/18/2023 3:35 PM | |
|
Joined: 7/15/2019 Last visit: 10/8/2025 Posts: 2 Rating:
|
Hello Everyone, Lately I'm facing a problem in a retrofit project where S7-200 CPU 226CN system is being upgraded to ET200SP CPU 1512SP system. In the existing system, there is a MP277 10" Touch Panel HMI which is needed to be communicated from new ET200SP PLC. HMI project backup has been migrated from WinCC Flexible to TIA v14 successfully. But during simulation of HMI RT in TIA v14 with ET200SP PLC, the HMI is found not communicating with the PLC. Here I'm attaching the test project backup where KTP700 Basic HMI and MP277 10" Touch HMI communicating simultaneously with S7-1200 PLC & ET200SP PLC. During simulation it is observed that MP277 10" Touch is communicating successfully with S7-1200 PLC but not with ET200SP PLC, whereas KTP700 Basic is communicating with both. Please help to resolve this communication issue Thanks in advance AttachmentTest Project 2.zip (282 Downloads) |
| 2/23/2023 10:05 AM | |
|
Joined: 8/3/2009 Last visit: 1/16/2026 Posts: 16644 Rating:
|
Hello do you connect your Multiplanel in simulation to the PLC Simulation? If yes this will not work: https://support.industry.siemens.com/cs/ww/en/view/109742764 -> The Image of the HMI is tool old to connect to PLC Sim V14 or newer But a communication to the real PLC should work. (I would not test with M -> use a DB with absolute addressing and activate the Put Get communication for testing) Bye Murof |
Last edited by: Murof at: 02/23/2023 10:07:06If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
|
|