Hi joppalomba, It seems to me that you are trying to load the PLC content into your TIA Portal as a new station. This requires that modules present in the device from GSD (ML), HSPs or Service Packs must be installed in TIA Portal on the PG/PC. So you have to get and install all the required GSDML files, which is sometimes difficult because many developers only provide the latest versions, but you need exactly the configured one. I searched the SiePortal and also the Keyence website for you and found the following: Kind regards |