Is it possible to use a S7-1500 Failsafe CPU with PCS7? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/03/2023 06:27:44New subject after splitting |
|
| 5/3/2023 3:37 PM | |
|
Joined: 2/17/2020 Last visit: 12/26/2025 Posts: 1251 Rating:
|
Hi, As of PCS 7 V9.0, the Industry Library supplies special blocks for exchanging data between S7-400 and S7-1500: IL - Application areas for the communication blocks However, there are no building blocks for communication with fail-safe S7-1500F. Direct communication between S7-1500F CPUs and F-Systems cannot be established. However, one can use any S7-300F/S7-400F CPU as a gateway. e.g. the IM151-8F CPU as the smallest possible. This can be connected to the S7-1500F as an I-Device and convert the data to S7 communication and pass it on to F-Systems. |
|