(1)| 5/14/2023 6:20 PM | |
|
Joined: 11/4/2015 Last visit: 1/7/2026 Posts: 16 Rating:
|
I have a different issue but related to this topic. On my block pins the Operator Level Authorization field is Disabled. Even though I have set the attribute correctly. ------------------------------------------------------------------------------------------ |
Last edited by: Zeesh1 at: 05/14/2023 18:21:03Last edited by: Jen_Moderator at: 05/15/2023 10:21:30New subject after splitting |
|
| 5/18/2023 11:09 AM | |
|
Joined: 3/14/2008 Last visit: 12/28/2025 Posts: 2233 Rating:
|
Hi Zeesh1, Did you set attribute s7_m_c for the parameter? If not, please do so. Also important is to set s7_m_c for the block itself, otherwise it would not be possible to use in WinCC because the block is not generated in tag management. Maybe that is the reason why the attribute remains greyed out. |
|
If I could help you, you can use the RATE button. Thank you. |
|
| 5/20/2023 6:54 AM | |
|
Joined: 11/4/2015 Last visit: 1/7/2026 Posts: 16 Rating:
|
Hi, I added S7_m_c to true for both pin and block. You can refer to the attachment. AttachmentOP_Level.pdf (445 Downloads) |
| 5/20/2023 7:19 AM | |
|
Joined: 3/14/2008 Last visit: 12/28/2025 Posts: 2233 Rating:
|
Hi, Set "OP_Level" to "Op_Level". |
|
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
|
|
| 5/20/2023 7:23 AM | |
|
Joined: 11/4/2015 Last visit: 1/7/2026 Posts: 16 Rating:
|
Thanks, it worked |