Hello, When I select camera communication settings to the Ethernet IP, I can connect the camera from my PC. But when I select profinet, I can not connect to the camera. It needs to be profinet because when I switch back to ethernet IP my PLC gives me error because of cannot reach to the camera. I have keyence SR1000 camera. My PLC is PLC : 1517f-3 pn/dp. Is there any solution to this topic? Thank you, AttachmentProblem.docx (489 Downloads) |
| 5/22/2023 11:53 AM | |
|
Joined: 1/21/2013 Last visit: 1/16/2026 Posts: 4405 Rating:
|
Hi, According to your drawing, you can't reach the Keyence sensor because it's on a different subnet than your computer. Starting with firmware version V2.8 of your PLC, you can use IP forwarding to make the sensor accessible to your computer. Kind regards |
| 5/22/2023 1:01 PM | |
|
Joined: 4/12/2023 Last visit: 7/17/2025 Posts: 16 Rating:
|
Connect means I can go online if connection is OK. |
Last edited by: AutoGen_113656 at: 05/22/2023 13:02:20 |
|
| 5/23/2023 7:35 AM | |
|
Joined: 4/12/2023 Last visit: 7/17/2025 Posts: 16 Rating:
|
I have found the problem. I just enabled the use router and than I wrote my PLC adress to here. Thank you for your help. |