Hello, I have seen a few answers from you where you mention that you useMod_rssimto simulate a MODBUS server. I tried it with myPLC 1214 DC/DC/DC, where I set my MODBUS Client function, but I couldn't connect the PLC with the simulator. In the data of my MB Client, I put the IP of my virtual machine since that's where I'm running the simulator, even so I also used the simulator from my real machine (I put the respective IP in the CONNECT parameter) and it didn't work. Do you know what it could be? I attach a picture of my CONNECT parameters. Thank you.
------------------------------------------------------------------------------------------ |
Last edited by: Francely at: 06/15/2023 20:40:35Last edited by: Jen_Moderator at: 06/19/2023 04:20:02New subject after splitting |
|
| 6/16/2023 7:15 AM | |
|
Joined: 4/28/2015 Last visit: 11/27/2025 Posts: 10970 Rating:
|
Hello,
your offline screenshot isn't helpful because some values can be already set with different values. Your problem I see in 2 options, as Client you need have Active establish connection set to true and set better remote port to 502 as MB TCP defines as standard. Next problem can be wrong network access rules set but this is what you need to correctly set if this is real problem. |
Last edited by: Duris_I at: 06/16/2023 07:18:07With best regards... |
|