Is it possible use OPC UA through CN1542-1? |
| 6/23/2023 11:33 AM | |
|
Joined: 3/11/2019 Last visit: 1/7/2026 Posts: 1653 Rating:
|
Hi, unfortunately it's not possible. It is not possible via another CP/CM, older firmware or older version of TIA. As an alternative you can use a router (like SCALANCE S615) to access OPC UA via another subnet. Access to OPC UA applications