I finally found the answer here: https://support.industry.siemens.com/cs/at/en/view/79993228 It says: "The S7-1500 CPUs und S7-1200 CPUs do not have private MIBs." As automationOperState OID belongs to the pivate AUTOMATION-SYSTEM MIB, it can not be used with an 15XX or 12XX CPU sysUpTime OID belongs to the standardized MIB II, and can thus be used with any type of CPU. |