(0)| 7/27/2023 4:53 PM | |
|
Posts: 4 Rating:
|
Hello everyone! Firstly my setup is: SINAMIC G120 - Control Unit CU250S-2 USS, SINAMICS Power Module 250 and I´m use the TIA V14 to configure the control. I'm trying to use the torque control with enconder in a induction motor that should be work as load for another machine. I configured the basics for torque control in software and initally I putted 0% as torque reference, however when a turned on the inverter , the inverter applies a dc current about 40A through the stator, for example, Is = 10A, Isb = 30A e Isc =-40A (Isa+Isb+Isc =0), even motor at standstill. That applied current is generating a resistance torque even with 0% of torque reference, thus the rotor is harder to spin. I think as the torque reference is null, that torque should not exists, the stator current should be 0A and the rotor should be "freer" to spin, right? I would like to know if that issues is normal and/or how I can configure the inverter to solve that issue. I attached some pictures. The fist one is he current through each motor phase (I measured once at ime, because i had one current probe) and the second one is the current at one phase and the speed from analog output port. Best regards Attachmentcurrent_pictures.pdf (563 Downloads) |
| 8/1/2023 5:09 AM | |
|
Posts: 126 Rating:
|
Hi esio eloi, Check out the post to solve the torque control issues here Monitoring and limit of the g120 parameter help to analysis the issue. Thanks
|