Is there a tutorial for saving alarm messages on MMC card? OP77B + WinCC Flexible 2005 SP1. Thank you. |
| 6/4/2009 9:44 AM | |
|
Joined: 9/28/2005 Last visit: 12/9/2025 Posts: 2957 Rating:
|
Hi, Its not possible with OP77B. You can use MMC card only for project backup. For alarms you need at least 277 OP. Look this post /tf/WW/en/Posts/30716#topthe same goes for OP77B. |
Last edited by: Darius at: 6/4/2009 9:46 AMBest regards, |
|
| 6/5/2009 10:19 AM | |
|
Posts: 289 Rating:
|
Thank you Darius. I have managed to write something on the MMC. First I have to use the GetDataRecordFromThePLC followed by ExportDataRecords. |