(0)| 10/21/2023 2:45 PM | |
|
Joined: 3/27/2008 Last visit: 12/30/2025 Posts: 1235 Rating:
|
Macro 41 has Din0 allocated to the run command. Parameter P0840(0) is the binary input for ON/OFF For DI0 = ON/OFF1, this is the Macro setting for the run command. For DI1 = ON/OFF1 For DI2= ON/OFF1, to make this the run command, make P0840(0) = r722.2. For DI3 = ON/OFF1 Tractor Attachmentallocate the run command.pptx (410 Downloads) |
|
Tractor |
|
This contribution was helpful to
|
|