(0)| 10/23/2023 6:18 PM | |
|
Joined: 3/7/2022 Last visit: 12/26/2025 Posts: 7 Rating:
|
Thank you for your fast response.. This issue appeared when I downloaded old backup on PLC1 that sent 62 bytes .. and then I downloaded a newer version that send 84 bytes. At the point I discovered the issues the plc2 has 24 bytes shifted (means data sent at adress 0 from plc1 i received it at address 24 at Plc2 .. but data sent from PLc2 are received with no issues at PLC1!!!) I read that using TCP connection is not recommended as Behavior of the TCP protocol: When data is transferred with the TCP, the transfer is data-stream-based. In this case no information is given about the length nor about the beginning and end of a message. This is not a problem when sending, because the sender knows how many data bytes are to be sent. The recipient however cannot tell where one message ends in the data stream and where the next begins. And I should use ISO on tcp instead if I want to determine start point and length. https://support.industry.siemens.com/forum/eg/en/posts/ag-send-between-s7300/74171 |