Dear all, I'm facing the following issue while uploading the PLC backup file from S7-1200 CPU(6ES7 214 1HG31-0XB0) in TIA Portal V16... ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/07/2023 04:56:56New subject after splitting |
|
| 11/6/2023 1:47 PM | |
|
Joined: 1/21/2013 Last visit: 12/30/2025 Posts: 4372 Rating:
|
Hi Robert, As you can see in the FAQ 'What options are available in STEP 7 (TIA Portal) for uploading when the project version in the CPU no longer matches the version on your PG/PC?', with TIA Portal V16 you can only upload a configuration from a device loaded with V16. In your case, you would need TIA V11 SP2 or TIA V12 to load the device into a blank project. This can be updated with V13 SP1/SP2 and then an upgrade to V16 would be possible. I know this is not an easy task as you need different operating systems to support the TIA Portal versions, but unfortunately this is the only supported method. Kind regards |