Hello, I am migrating from a S7-300 (circa 1994) to S7-1500 (v17) I am encountering the issues below and have some difficulty resolving them. 1. Temporary Tags can only be addressed symbollicaly. 2. Tag P##x_record not found or not addressable via operator P# 3. Syntax Error: the specified value "IOID" is invalid 4. The instruction accesses the DB or the DI register, However, you have not opened a data block in this register. 5. Jumps from Boolean Logic sequences are only permitted with jump instructions that set the status bit "/FC" AttachmentMigration.pdf (371 Downloads) |
| 10/18/2023 1:47 AM | |
|
Joined: 10/7/2005 Last visit: 12/29/2025 Posts: 3052 Rating:
|
IOID is easily solved by getting rid of it. WR_REC (SFC58) in S7-300/400's had this parameter and required it together with the LADDR parameter (use F1 in classic Step 7 on WR_REC to get its context sensitive help for more). WR_REC in S7-1500 doesn't need nor has the IOID parameter anymore and only uses/requires the LADDR parameter (which is now the HW identifier as type HW_IO, again, use F1 in TIA Portal Step 7 on WR_REC to get its context sensitive help for more). It would help to also see the original classic S7 program (whole block with incl. variable declaration) to help with any other unresolved issues plus whole block incl variable declaration of the converted TIA portal program. |
|
Cheers |
|
This contribution was helpful to
|
|
| 12/11/2023 4:33 PM | |
|
Posts: 7 Rating:
|
IOID solved, thank you. For issue 5 I'm still struggling. Getting the error for Networks 4-16 (some have multiple) all the same error. AttachmentFC22.pdf (347 Downloads) |