hello, i'm trying to make two different protocols on the same PLC, one profinet, no problem, and one modbus, but i can't figure out if it's possible or not. ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 12/12/2023 13:52:53New subject after splitting |
|
| 12/12/2023 2:54 PM | |
|
Joined: 9/27/2006 Last visit: 1/14/2026 Posts: 12480 Rating:
|
Hello lilouf; Towone is quite correct, parallel protocols on TCP/IP can be implemented on S7 PLCs, either on yhe Profinet integrated port of the CPU or using Ethernet CPs. Look at this document, showing how to implement Modbus TCP exchanges between S7 CPUs over the integrated Profinet port. Profinet exchanges are not inhibited by the use of Modbus TCP functions uiu can still use them in parallel. https://support.industry.siemens.com/cs/ca/en/view/102020340 Hope this helps, Daniel Chartier |