Hello TEJCOOL; This application example will give you documention and a sample project for PUT/GET functions between 2 S7-300 CPUs. https://support.industry.siemens.com/cs/ca/en/view/82212115 Your S7-317 using a CP 343-1 must act as a client in ths project, while the S7-315 with a CP 343-1 LEAN must be configured as a server. Look at the documentation file, study the description of the S7-300 configurations. There is a chapter based on TIA Portel, another one on Step 7 v5.6,. Then select the appropriate sample program and use it to understand the configuration and programming of your CPUs. Hope this helps, Daniel Chartier |
This contribution was helpful to
|
|
| 12/21/2023 2:35 PM | |
|
Posts: 3 Rating:
|
Hi Daniel, Thanks for the information! That was really helpful. |
Last edited by: TEJCOOL at: 12/21/2023 14:38:21 |
|
| 12/22/2023 6:46 AM | |
|
Joined: 7/9/2015 Last visit: 1/7/2026 Posts: 4493 Rating:
|
Hi TEJCOOL, I can recommend you a very good manual. Please check table 21.4.2 S7300/S7-300 on PDF Page 103. Ther you can read, that in PLC with CP Lean is only server. CPU-CPU Communication with SIMATIC Controllers Regards, Towome |
|
|
|