ZumoPLCero The maximum number of possible communications is a fixed value that cannot be changed. However, depending on the type of communication protocols used, there may be other ways to increase the number of connectable partners. Your PLC allows up to 16 connections based on S7 communication and an additional 16 connections for Open User Connection (OUC). Using the SIMATIC S7-300 Ethernet CP with multiplexing support is one way to increase the number of S7 communications. The other possibility is to replace the CPU with e.g. CPU 317-2 PN/DP, which allows 32 S7 connections. Kind regards |
This contribution was helpful to
|
|
| 1/11/2024 7:43 AM | |
|
Joined: 8/3/2009 Last visit: 1/15/2026 Posts: 16638 Rating:
|
Hello ZumoPLCero check out this information in Chapter 11.5: https://support.industry.siemens.com/cs/ww/en/view/45531110 Bye Murof |