same problem i tried to communicate to communicate tp900 comfort HMI with s7 1200 plc but error" $ 140023 Error during synchronization: The system time of PLC HMI _connection_1 could not read" even tp900 hmi can not communicate with PC, pinging ok what is an issue. Waiting for reply ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 01/12/2024 09:51:18New subject after splitting |
|
| 1/12/2024 11:33 AM | |
|
Joined: 8/12/2021 Last visit: 1/15/2026 Posts: 351 Rating:
|
Hi! I'm afraid it would be necessary to answer the questions in the previous forum thread. Maybe you can find more help here. |
Last edited by: The Helping Hand at: 01/12/2024 14:53:14Text formatting optimized If this Information really helps, you could use the Rate function |
|
| 1/17/2024 1:43 PM | |
|
Joined: 8/3/2009 Last visit: 1/16/2026 Posts: 16644 Rating:
|
Hello Jashu24 It would be interesting if you get only this error or if your PLC connection to the HMi is also down (do you get Tag values in HMI?)? If you have general problems with the connection then this time synch error is just a because the communication is down. Check if everythinig is OK configured: https://support.industry.siemens.com/cs/de/en/view/89852595 https://support.industry.siemens.com/cs/de/en/view/109803668 Bye Murof |
|
If this Information really helps, you could use the Rate function |
|