Hi youssouf-attia, The number of possible devices depends on the CPU used. If you are talking about remote stations, you are probably talking about PROFINET IO devices. For example, for a CPU 1515-2 PN, the technical data will show a maximum of 256 devices. For HMI devices, the number depends on the type of HMI and the connection. A mid-range to high-end CPU should be able to connect 5 HMIs, but you should also consider the amount of data. Compared to an IO device, the amount of data is much higher and therefore the communication performance may be poor. Kind regards |