Hi, I'm facing similar situation here , we have rdb160bn thermostats connected to Pxc7.e400s controllers. How do we discover these devices. Thanks in advance ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/18/2024 12:03:12New subject after splitting |
|
3/16/2024 4:34 PM | |
Joined: 11/8/2017 Last visit: 10/8/2024 Posts: 337 Rating: (190)
|
Hi, You can use a BACnet browser whilst connected to the PXC7's ethernet port. Provided that the MSTP settings on the PXC7 and RDBs are correct, the BACnet browser will allow you to discover the RDBs, and also the points within them. This is good for proving that the network installation and settings etc are correct, and that all devices are visible to / from the PXC7. Alternatively, you can refer to the documentation for the RDB (which is attached, start at page 28) to create points within the BACnet References section of the PXC7 engineering tab within ABT. Some BACnet browsers will allow you to export an EDE file. The EDE file contains the mapping info for discovered devices and their associated points, and can be imported into ABT within the BACnet References section. This can save you some time, rather than manually creating points within ABT. Regards, AttachmentA6V11989976_BACnet Room Temp Controller RDB160BN_en.pdf (251 Downloads) |