What is your CFC editor version? may be check the latest available version here.https://support.industry.siemens.com/forum/nl/en/posts/simatic-pcs-7-software-updates/189882/?page=0&pageSize=10 Another idea is 1. Try to create a new project via new project wizard, add random hardware and address into the hardware config and add random chart in cfc editor. Compile and do the same thing again by selecting the cross reference. To check whether is the software issue or project issue. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
This contribution was helpful to1 thankful Users |
3/22/2024 3:45 AM | |
Joined: 9/9/2015 Last visit: 9/25/2024 Posts: 727 Rating: (278) |
Then the next step could be method of elimination. Remove the blocks/files one by one. After you removed the blocks /charts, remember to go CFC editor -> options -> Block types -> clean up the database for both offline block folder and chart folder (Chart database). What i see is some files for the block types are missing. You might need to check the properties of the blocks, find all related FC/FB that related to the blocks. Ensure all are inside your project folder. |