Hi dsaegon, in the documentation to the FAQ, you can read in chapter 1: The information in this document is valid for the following F modules of the ET 200SP in the central and distributed configuration: … So why do you believe it would not work with a central configuration? Have you tried it? When continuing reading the documentation, you will find the description of the block parameters in chapter 4.
Kind regards |
This contribution was helpful to
|
|
| 9/6/2022 7:11 AM | |
|
Joined: 9/24/2021 Last visit: 11/19/2025 Posts: 23 Rating:
|
Hi all. I've contacted with the Siemens support Department and it seems it is not possible to do the assignment from a central PLC with the F-capability enabled. I paste the response of the supporter with the options available to achieve it. "Sadly there is no other option to assign the failsafe addresses using the PLC's program. Kind regards!. |