For establish communication between LCCF Scanner function to FANUC robots, we have a PPT slideshow. There's some useful information in there. If it helps someone, I'll be happy. For example code published by Hristoffy EnetScanner S7_1500-Fanuc.zip, My suggestion is call LCCF function from OB30 with cyclic time around 5,000 - 7,000 µs = 5-7 ms. You can play with this, but look for PLC cycle time. Even with 11 robots we had packetinterval for each robot at 140ms with stable connection. AttachmentSiemens_Ethernet-IP_scanner_V05_commissioning_instructions.pptx (1051 Downloads) |