10/1/2024 11:42 AM | |
Joined: 10/6/2022 Last visit: 1/31/2025 Posts: 60 Rating:
|
It's a running machine and I don't want to re-initalize DBs and such. |
10/1/2024 12:50 PM | |
Joined: 7/9/2015 Last visit: 8/29/2025 Posts: 4443 Rating:
|
Hi, please have a look to the following link - there you see which kind of change PLC will go to Stop or DB will re-initialized. PLC stays in run if you revise comments (new, revised, deleted) with the exception of comments in the HW configuration...(S7-1200 V4.0 or higher/S7-1500). Downloading blocks in the "RUN" operating mode to the device Regards, Towome |
Last edited by: Towome at: 10/01/2024 12:51:25
|
|
10/1/2024 5:25 PM | |
Joined: 10/6/2022 Last visit: 1/31/2025 Posts: 60 Rating:
|
Unfortunately I cannot open this link in my region |
Last edited by: Figuren at: 10/01/2024 17:26:00 |
|
10/2/2024 5:46 AM | |
Joined: 3/30/2020 Last visit: 9/15/2025 Posts: 5447 Rating:
|
There is a good chance that the message you see displayed is an annoyance message. Closing the message has no influence on the page rendering. Try again with this link:
|
Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to
1 thankful Users |
10/2/2024 5:54 AM | |
Posts: 3 Rating:
|
Yes, you can add comments to Tags in both IO-list and DBs, and download without issues as long as the format is supported by your software. |