HI, did you setup the connection information, access point in pg/pc interfaces as well, correctly? Following FAQ may help: Testing and simulating HMI projects (TIA Portal) in conjunction with SIMATIC controllers, PLCSIM and PLCSIM AdvancedEven its for unified, check the interface settings and access point Establish connection between simulated CPU S7-1500 (S7-PLCSIM Advanced) and WinCC Unified PC RuntimeIn addition to that, check if in CPU configuration the checkbox for "Allow only secure pg/pc communication...." is set. If yes, disable this option and download the hw config to PLCSIM again. regards sancruz |
|