Hi, as from TIA V18 (with the new CPU’s FW), there is available a new block, Ramp Soak). RampSoak instruction is a ramp function that generates “an output value that follows a configurable profile on a time-dependent basis. Every point of this profile has a target value and a time value. When the profile is executed, the target value of the current point is reached within the time value.” (see more details in the TIA System Help in, Information System, Program a PLC, Instructions, Technology, PID Control, RampSoak). TIP:
Configuration steps
In this example, the points and commands are set in the WhatchTable1 and the result monitored in the Trace1 AttachmentProject4_20221205_0733.zip (288 Downloads) |