What is the minimum distance required between a Profibus and Power Cable for laying? |
| 7/2/2009 9:10 AM | |
|
Posts: 8946 Rating:
|
200 mm. |
This contribution was helpful to
|
|
| 7/2/2009 9:13 AM | |
|
Posts: 487 Rating:
|
Hi Could also pull the profibus cable in a metal pipe. Eric |
This contribution was helpful to
|
|
| 7/2/2009 10:41 AM | |
|
Joined: 7/2/2008 Last visit: 12/21/2025 Posts: 929 Rating:
|
Hello NBRM, Please look at the attached file which has been extracted from PROFIBUS Installation Guideline for Cabling and Assembly. You can download the original document from this link. I think it will be useful for you. Best regards. H-H AttachmentRouting Profibus cables.pdf (253 Downloads) |
| 7/2/2009 12:11 PM | |
|
Posts: 262 Rating:
|
Hi, |
| 7/2/2009 12:22 PM | |
|
Posts: 160 Rating:
|
Apart from getting Standards from the Profibus International website you can also look at the following manual from Siemens http://support.automation.siemens.com/WW/view/en/35222591 Have a look at Section C for details about installing Profibus Cabling |
This contribution was helpful to
|
|
| 7/3/2009 11:16 AM | |
|
Joined: 10/7/2005 Last visit: 1/16/2026 Posts: 3054 Rating:
|
And just to round things off: There is an excellent web based Profibus training course available (for free!) on the PI website (www.profibus.com). The direct link to this course is: http://www.profibus.com/fileadmin/media/wbt/en/wbt1/index.html |
|