7/1/2009 12:24 PM | |
Joined: 9/27/2006 Last visit: 11/18/2024 Posts: 12296 Rating: (2691)
|
Hello amateur; It all depends on how you define "merger". Communication of data between two systems is always possible, and interlocking data can be exchanged between the old system and the new S7-400H. If that is the extent of your needs, it should be relatively easy to implement. The S7-400H Fault-Tolerant Systems manual discusses the issue of communications between a S7-400H redundant system and a non-redundant CPU quite in depth. Here is a link: http://support.automation.siemens.com/WW/view/en/1186523 And here is how the subject is introduced: 8.5 Communications via S7 Connections Communications with standard systems Fault-tolerant communications are not possible between fault-tolerant and standard systems. The following examples illustrate the actual availability of the communicating systems. Configuration Standard connections are configured with STEP 7. Programming If standard communications are used on a fault-tolerant system, all the communication functions apart from “global data communications” can be used for them.The standard communication SFBs are used for programming communications with STEP 7. If you had thought about a different level of integration between the 2 systems, maybe you could provide more details. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 7/1/2009 12:54 PMLast edited by: dchartier at: 7/1/2009 12:25 PM |
|