7/14/2021 12:58 PM | |
Joined: 9/12/2019 Last visit: 1/31/2025 Posts: 3 Rating:
|
Hello sir, Iam also facing the same problem with my S120 single motor module controlled by CU320-2P.Since it is book size model i checked the X21-3,4 for 24v and found ok. But still the r2 shows [44]switching on inhibited-supply STO terminal w/24 V (hardware).So it will helpful if someone give solution to solve the issue. Here by attached documents of Missing enables,P9601,P9620,r46.8,Safety integrated functions and Status word. ------------------------------------------------------------------------------------------ AttachmentATTACHMENT.docx (709 Downloads) |
Last edited by: Jen_Moderator at: 07/14/2021 13:30:41New subject after splitting |
|
7/14/2021 4:19 PM | |
Joined: 7/7/2010 Last visit: 9/5/2025 Posts: 16061 Rating:
|
Sounds like this system has been running for a while and you want to figure out why it is not being allowed to run now. True? If that is true, the E-Stop / safety string for the drive (check the control unit digital inputs for the safety integration and EP+ terminals on the Power module. These are well disguised (my opinion), sometimes behind covers.
|
science guy |
|
7/16/2021 1:11 PM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Can you attach drive back up (project) file here. |