Hi Guys. I have a 6ES7 214-1AH50-0XB0 V1.0 s7 1214 G2 CPU. I have a 6ES7 241-1CA50-0XB0 V1.0 CB 1241 (RS485) communication card plugged on it, but when I install the hardware I get the error "Hardware component not available due to type mismatch" and the PLC does not run. I am using tia portal v20 update 3 . https://support.industry.siemens.com/cs/ca/fr/view/72341852/en I downloaded the HSP updates from this link. |
Last edited by: Moderator_Lan at: 08/14/2025 06:07:34link optimized |
|
8/13/2025 9:16 PM | |
Joined: 6/23/2024 Last visit: 8/20/2025 Posts: 5 Rating:
|
I tried it with 2 different cards and the result was the same.
AttachmentDiagnostics.txt (32 Downloads) |
8/14/2025 11:43 AM | |
Joined: 3/30/2020 Last visit: 9/5/2025 Posts: 5427 Rating:
|
The configuration you have in Step7 / TIA Portal is good. Find the firmware you need to load from here:
Do these notes push the topic forward? |
Last edited by: qwazee at: 08/14/2025 11:46:24Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to
1 thankful Users |
8/14/2025 1:05 PM | |
Joined: 6/23/2024 Last visit: 8/20/2025 Posts: 5 Rating:
|
Thank you, the problem was solved after updating the firmware. |
This contribution was helpful to
3 thankful Users |