Hi! Thats one super quick responds. |
|
A small step is also a step. |
|
| 12/19/2025 11:00 PM | |
|
Joined: 5/4/2009 Last visit: 12/21/2025 Posts: 916 Rating:
|
Great, but how can we access the "Coordination" area pointer? |
|
Aim Higher |
|
| 12/20/2025 12:36 AM | |
|
Joined: 9/27/2006 Last visit: 12/26/2025 Posts: 12474 Rating:
|
Hello Tomy; To monitor the status of an HMI you must use a "coordination area pointer" in WinCC: start by configuring the area pointer as shown here: https://support.industry.siemens.com/cs/bg/en/view/109794203/43421366283?dl=en The coordination area pointer in WinCC uses a length of 1 Word. For example: https://support.industry.siemens.com/cs/bg/en/view/109794203/39382950155 In Step 7 you read the 3 LSB (least significant bits) in your program, at the address you set for the area pointer, Bit 2 of that address will tell you if the H'MI is ocnnected or not. Bit 3 sends a pulsed lifebit that you can follow to ensure the HMI is still active. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 12/21/2025 14:04:48 |
|