Hello EddieBauerABInBev, As per the manual: A0910 Vdc-max controller de-activated Cause Vdc max controller has been de-activated, since controller is not capable of keeping DC-link voltage (r0026) within limits (P2172). - Occurs if main supply voltage (P0210) is permanently too high. - Occurs if motor is driven by an active load, causing motor to goes into regenerative mode. - Occurs at very high load inertias, when ramping down. Diagnosis & Remedy Check the following: - Input voltage (P0210) must lie within range. - Load must be match. Please check that the parameters of quick commissioning is correct. Do you have over voltage relay or how did you know that the supply voltage is within limit. You can also reset the drive to factory settings and then put again quick commissioning parameters (motor and supply) parameters and see what will happen. Hope this helps. |
|