Dear Zenta, Thank you for your reply. Actaully the problem is how to read, let's say 1000 data and transfer them to the PLC as quickly as possible. Thus, how to initalise the power tags from the archive for the type ARRAY? Regards, Dejan |
| 11/18/2009 2:59 PM | |
|
Joined: 10/12/2006 Last visit: 12/4/2025 Posts: 206 Rating:
|
Dear Dejan, sorry my mistake... I see the problem... I check something, and if its working I write it. Regards Zenta |
| 11/19/2009 10:48 AM | |
|
Joined: 5/2/2006 Last visit: 10/3/2025 Posts: 3 Rating:
|
Do you have a license forrecipesinWinCC flexible Runtime? If yes then you can use a recipe! Use standard functions ImportDataRecords and ExportDataRecordsinstead of scripting. Suggest to first export a Recipe so that youknow the header settings. You can built the elements of the recipe (tags) with internal or external (array) tags. When you use internal tags youcan use different CSV files to import the values andthen copy to plc. |
| 11/19/2009 7:52 PM | |
|
Posts: 5 Rating:
|
Hi cle, Thanks for tip. I will investigate in that way because with script I am stucked and don't know what to do else. I will inform You if I get some result. regards Dejan |