Hello, Does the communication between between the CPUs via integrate PN interface work????You can use for example S7 communication between the twoCPU 315-2PN/DP http://support.automation.siemens.com/WW/view/en/18516182 http://support.automation.siemens.com/WW/view/en/18610307 Does the communication to the SCADA system work??? . MPI address forcommunication via Ethernet sounds strange. Which function blcoks for communication do you use??? |
| 12/15/2009 12:57 PM | |
|
Joined: 10/7/2005 Last visit: 1/16/2026 Posts: 3054 Rating:
|
Hello RFP simply ignore the "MPI_ADR" parameter of FC100 (SWR_START), its value is irrelevant if you use anEthernet (ISO) connection (or Profibus FDL) betweenthe two CPU's of your Software Redundant (SWR) system (just like the "LADDR" and "VERB_ID" parameters are irrelevant if you use MPI). Your main problem at the moment though is that you can't use the onboard PN port for the redundancy link between the two CPU's and will require a CP for it (unless you ask Siemens kindly to release an updated SWR package that supports the PN port, since it has been 6 yeasr since the "current" version 1.2 came out). Chapter 4.7 of the SWR manual list the possible networks and hardware requirements (and incorrectly calls the Ethernet CP a "CP 345-1" instead of CP343-1 but nevermind). I hope this helps |
|