2/9/2010 1:56 PM | |
Joined: 2/6/2009 Last visit: 8/19/2024 Posts: 939 Rating: (118) |
HI, If the DP slave fails which is connect to the Master CPU then the CPU will switch over to the reserve one. Please see the pages 44&45 for your reference in the attached manual.
AttachmentSwr_english.pdf (316 Downloads) |
_______________________________________________________________ |
|
This contribution was helpful to1 thankful Users |
2/9/2010 3:19 PM | |
Posts: 157 Rating: (10) |
Thank you saravana very much But, is this manual applies also for S7-400 H??? I think the redundancy rules is different, isn't it??
Regards, |
2/9/2010 11:45 PM | |||||
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (309)
|
Dear all,
What will happen is stated in S7-400H manualin Chapter13 (13.3.2 Failure and replacement of a redundant PROFIBUS DP interface module).
So, a Master/Reserve change over doesn't take place. You can also read in the manual page 82,
Best regards. H-H |
||||
This contribution was helpful to2 thankful Users |
2/12/2010 5:23 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (309)
|
Hello Bilal,I'm glad I could help you. Thanks for your nice words.
In Addition to what Nil had already said, I had the chance to testit yesterday andpulled out the Profibus bus connector from the master CPU and it was still the master.
No. Why would you do this?! This thread will show you an idea of how to stopthe masterCPU but Techyand Arethad totally different applicationsfrom what you have. In your case, I would never stop any of the 2 CPUs. Just let it work the way it's designed. Best regards. H-H |
This contribution was helpful to1 thankful Users |
2/13/2010 8:07 AM | |
Posts: 157 Rating: (10) |
Thank you very much Nil96 & H-H That was very helpful for me.. Regards,
|
This contribution was helpful to2 thankful Users |