Hi, just noticed, the diagram I posted inthis threadshows the generation of the A034 alarm. It occurs when a deviation is detected between the setpoint and the actual. You can limit most things in the drive, but it is good software practice to limit the user input in the first place. Even if you set a limit in the drive, the setpoint will still be transmitted to the drive which because of your limit will never be achieved, so A034 all over again. What exactly is the value on the HMI you refer to? Is it percent? Regards, Graeme
|