(0)| 8/2/2010 9:23 AM | |
|
Joined: 4/29/2010 Last visit: 1/20/2025 Posts: 1557 Rating:
|
Hello, yes this is possible. Please take a look at this faq wich explain the multiplexing in flexible: http://support.automation.siemens.com/WW/view/en/21807421 best regards |
| 8/28/2010 11:41 AM | |
|
Posts: 63 Rating:
|
Thanks For your reply, I know that thing but my question is "How can i reduce the number of Power Tag using Tag Multiplexing???" Hope u understand and help me |
| 8/28/2010 1:15 PM | |
|
Joined: 10/7/2005 Last visit: 12/29/2025 Posts: 3052 Rating:
|
You can't dear The Mack, for that you would need to use Address Multiplexing instead (see HERE for more). Other ways to reduce the tag count would betouse Array tags or bundle Boolean's into WORD's or DWORD'sand I hope this helps. |
|
Cheers |
|