Posts: 4 Rating: (0) |
i am having a problem with our VFD Micromaster 430 showing in the BOP ( P---- ). can anybody help me isolate this problem.. thanks |
12/3/2010 11:08 AM | |
Posts: 739 Rating: (55)
|
you are using a wrong operator panel (BOP) If you plug a BOP to a MICROMASTER MM430, or a BOP2 to a MICROMASTER MM440 or MM420, then "- - - - -" is displayed. BOP Basic Operator Panel [6SE6400-0BP00-0AA0] for MM420 and MM440 BOP-2 optimized Operator Panel [6SE6400-0BE00-0AA0] for MM430 See FAQ: http://support.automation.siemens.com/WW/view/en/23623849 |
12/7/2010 10:21 AM | |
Posts: 739 Rating: (55)
|
this indicates a fault in the 24V power supply - this answer is published in the suggested FAQ (above). |