(0)| 2/2/2011 10:31 AM | |
|
Posts: 100 Rating:
|
Hi to all. I am using KTP 600 Basic color DP 6AV 6647-0AC11-3AX0. HMI have one serial port. HMI have the following set points in Control panel 1. MPI/Profibus setting - 187.5 Kbps 2. Communication -- MPI/Prifibus is checked. I have attached wicc flexible connection settings& PG/PC interfacedetailsbelow. i am using PC ADAPTER USB cable to download the program. I already downloaded the program in this(same) HMI. but now its not downloaded. In pc adpter usb cable usb lamp is slowly blinking.Using this same cable communication is establisedwith PLC. I checked with all the baud rate combination.(187.5 Kbps & 19.2 Kbps) How can i download the program in to this hmi. Regards, L.V.Sundar Attachmentktp 600.zip (150 Downloads) |
| 2/2/2011 10:46 AM | |
|
Joined: 4/29/2010 Last visit: 1/20/2025 Posts: 1557 Rating:
|
Hello, for example you have set the same MPI adress for your pg und for the KTP600. USB-converters also aren`t released for such connection. I advice you this FAQ: http://support.automation.siemens.com/WW/view/en/23802404 best regards. |
Last edited by: Sandman at: 2/2/2011 10:47 AM |
|