(0)| 2/9/2011 10:21 AM | |
|
Posts: 4 Rating:
|
|
| 2/10/2011 6:51 AM | |
|
Joined: 10/7/2005 Last visit: 1/12/2026 Posts: 3054 Rating:
|
Hello Georgee the best advise I can give you is to start by having a look at chapter 11 of the SIMATIC Fault-tolerant systems S7-400H manual. I hope this helps |
|
Cheers |
|
| 2/15/2011 8:22 AM | |
|
Posts: 37 Rating:
|
You'll need 4 CP443-1 cards, 1 for each processor and redundant wiring between each pair (0 pair and 1 pair) |
| 2/15/2011 8:51 PM | |
|
Posts: 947 Rating:
|
enough 2 CP443-1 (1 CP443-1 on rack) and switch |
| 2/16/2011 2:04 AM | |
|
Posts: 37 Rating:
|
If there is only one CP on each rack it removes redundant communication and removes all communication if a CP card becomes faulty. |
| 2/16/2011 8:21 PM | |
|
Posts: 947 Rating:
|
in this case connection work by other (not fault) CP and optical link CPU |
| 2/22/2011 1:03 PM | |
|
Posts: 28 Rating:
|
If it is just for information exchange you can use a y-link and connect a dp-dp coupler for communication between the two systems. |
| 2/23/2011 9:36 PM | |
|
Posts: 947 Rating:
|
СPU 400H work as master. This sheme (Y-link, dp-dp coupler) not work |