Hello... You cannot use S5 cable for connecting 810....you need to use RS232 cable for this....check the attachment for the RS232 cable configuration.... Check this link for more infromation in 810: /tf/WW/en/Posts/50916 AttachmentRS232 serial cable.pdf (669 Downloads) |
| 5/31/2011 4:51 PM | |
|
Joined: 1/19/2008 Last visit: 10/20/2025 Posts: 998 Rating:
|
HI, You do not need TTY. Siemens 810 is RS232 V24 for S5 as well as PCIN. Same cable. Pee |
| 5/31/2011 8:39 PM | |
|
Posts: 594 Rating:
|
check this manual for the cable http://support.automation.siemens.com/WW/view/en/22089954 do not forget to start data transfer, if you want to go online with Step5 |
| 6/1/2011 7:25 AM | |
|
Posts: 4 Rating:
|
thank you MBA I'll try to make a cable according to the schema documentation. for data transfer I have no problems. is to link programming TTY it not work. |