(0)| 7/10/2011 4:17 PM | |
|
Posts: 18 Rating:
|
help,CH_AOblockinterconnects I get awarningthe attached AttachmentSIMATIC 400_Module driver.pdf (130 Downloads) |
| 7/10/2011 5:32 PM | |
|
Posts: 18 Rating:
|
hello checkthe connectionis wellattachedgraphics Attachmentconection.pdf (110 Downloads) |
| 7/11/2011 10:11 AM | |
|
Posts: 836 Rating:
|
Hi, i did the same configuration as you and not getting this warning when i connect the value parameter. Have you tried to compile the program again? |
| 7/13/2011 11:03 PM | |
|
Posts: 2661 Rating:
|
Make sure the data type for the address in the Symbol Table is WORD. |
| 7/28/2011 8:53 PM | |
|
Joined: 9/14/2006 Last visit: 1/15/2026 Posts: 5 Rating:
|
the address you connect is PQW which is not supported by Channel driver, please use QW in your symbole table |