(0)| 6/21/2011 10:23 PM | |
|
Posts: 75 Rating:
|
Hello everybody! Anibody have sucess in connection between S7-315 2-PN/DP and Danfoss VLT302 via MCA120 Profinet card? I am try to use this solution, but have a message warning W34 and not see any value on status/control word display! Anibody have any ideia about this? Thanks for any help Splitted from Profinet Communication through a danfoss drive.
|
Last edited by: O_Moderator at: 6/22/2011 12:26 PMnew subject after splitting |
|
| 6/22/2011 11:34 AM | |
|
Joined: 4/24/2006 Last visit: 1/15/2026 Posts: 9105 Rating:
|
Dear NewTech, Please check the IP address and Device Name (host name). Have a look at this link: http://mcliterature.danfoss.com/WebPublish/doc_MG90U202.pdf Best regards, Wizard |
| 10/28/2011 11:34 AM | |
|
Posts: 2 Rating:
|
I have the same problem with connection. NewTech, how did you solve the problem? |
| 11/1/2011 12:06 AM | |
|
Posts: 75 Rating:
|
I solved this problem by reversing the control and status words... and direct write status by danfoss manual..AttachmentCreate UDT.pdf (683 Downloads) |
| 11/1/2011 12:15 AM | |
|
Posts: 75 Rating:
|
Invert byte!
|