HelloRAJKIRAN, No, you can't manage I/O redundancy in a single module.
If you mean the software redundancy package (warm standby) then again it's not possible. I/O redundancy is only available with H-System. If you mean developing a software solution then I believe it is still not going to work. You can write a simple code to split the analog output value into 2 equal values like what the REDIO blocks do for you but what channel error will you be able to catch in order to produce a the complete value from the healthy channel?. In analog outputs it's always a module redundancy concept. I mean channel errors are kind of negligible and the REDIO concept is depending on module failure. Best regards. H-H |
This contribution was helpful to
|
|
| 11/28/2011 10:50 AM | |
|
Joined: 8/18/2009 Last visit: 7/28/2025 Posts: 558 Rating:
|
Thanks H-H, I have used 2 AO Card for H-redudancy. |
|
Rajkiran Patil |
|
This contribution was helpful to
|
|
| 11/28/2011 11:59 AM | |
|
Posts: 4 Rating:
|
Dear Rajkiran, right for H-redudancy for every module required 1 module in another rail. |