12/5/2011 8:09 AM | |
Joined: 8/18/2009 Last visit: 6/17/2024 Posts: 548 Rating: (33) |
Please tell me from which Manual or doc. i will get all information regarding this point |
Rajkiran Patil |
|
12/5/2011 9:40 PM | |
Joined: 10/7/2005 Last visit: 10/14/2024 Posts: 3024 Rating: (1054)
|
Hello RAJKIRAN perhaps the FAQ collection below on this subject will be of interest for you too: H Technology CPU 41x -- Operation and maintenance -- Querying status |
Cheers |
|
This contribution was helpful to1 thankful Users |
12/6/2011 7:33 AM | |
Joined: 10/7/2005 Last visit: 10/14/2024 Posts: 3024 Rating: (1054)
|
Hello RAJKIRAN have you downloaded the "H_status.zip" step 7 library from the link? It contains FB 523 and while the pdf shows an example CFC call of it, you can of course call itinany language you'll like and FB 523 is NOT limited to PCS7 use only. Having said that, all that FB523does, is essentially calling SFC51 RDSYSST withSZL-ID W#16#xy71 (plus some ALARM-8P handling which you may not need or want). If you look up the help on SFC51 you can also developyour own H status evaluation block. I hope this helps |
Cheers |
|